Post by nadjim on Oct 30, 2020 4:25:05 GMT -8
SLC5/04. Is it possible to put a bridge with the remaining port for IP Ethernet communication?
If you have an idea
Thank you
|
|
|
Post by Admin on Oct 30, 2020 10:06:21 GMT -8
|
|
|
Post by nadjim on Nov 2, 2020 3:30:22 GMT -8
Unfortunately my rack is full. is it possible to use the 1761-NET-ENI with the remaining port ??
|
|
|
Post by Admin on Nov 2, 2020 4:37:50 GMT -8
Your best solution in the ethernet module (You may need to free up a slot on your PLC, or purchase the next size rack off ebay for example for less than a $100). Since Rockwell Automation® discontinued the 1761-NET-ENI, for just simple data extraction (not upload/download) if you want that peer to peer communication, you can use any 3rd party DF1(RS232 9pin port) to Ethernet converter. Like the PLX51-DF1-MSG by Prosoft or Alpha-Link17000-DEIP by AlphaNet.
|
|
|
Post by nadjim on Nov 2, 2020 5:26:18 GMT -8
thank you for all these explanations, but the (RS232 9pin port) is already used. I only have one free port left (see the photo above ).
|
|